plc1214c connection ktp 600 dp ? Thank you. |
| 1/8/2012 2:58 PM | |
|
Posts: 1742 Rating:
|
Hello, An S7-1200 does not have a built-in Profibus Interface by default. You could add a communication module CM1243-5 for that: From the system manual p446: http://support.automation.siemens.com/WW/view/en/36932465 The CM 1243-5 DP master module supports the following additional communications services: ● S7 communication –PUT/GET services The DP master functions as a client and server for queries from other S7 controllers or PCs via PROFIBUS. –PG/OP communication The PG functions allow the downloading of configuration data and user programs from a PG and the transfer of diagnostics data to a PG. Possible communications partners for OP communication are HMI panels, SIMATIC panel PCs with WinCC flexible or SCADA systems that support S7 communication. |