Hi, I would use the fixed frequency selector to switch between High and Low speeds when the limit switch drives a digital input. See the attachment. You cannot change the Overcurrent Limit of the drive, however, you can change other parameters which may cause an overcurrent. Firslty, confirm all motor data settings are correct, run the MotID to impove the motor model. You can increase ramp up times or reduce the P gain settings (if practical) in order to reduce the occurrence of overcurrents. Check the setting of P640 (Motor overload) this can be upto 400%, although I would not recommend this much. Regards, Graeme