Yes, you can do this using Dataset Switch over You have to use P810 for that But before doing this, Copy CDS datas to index 1 P809.0 - 0 P809.1 - 1 P809.2 - 1 Set P701-99 (Enable BICO for DI 1) P810 - 722.0 (Switch to dataset 1 when DI 1 is high) Set P1000.1 - 3 (fixed Frequency) P1000.0 - 2 Analog setpoint P1001- 15 Hz P1016 - 1 P1020- 1 Also have a look at following FAQs MICROMASTER 4, SINAMICS G: Working with different drive data sets DDS / command data sets CDS How do I use different parameter sets with the MM440/MM430? Regards Devesh Vithani |
|