Hello kelese yes it does and every PROFINET device on a Network must have a unique: - MAC address (unique by factory default) & - Device Name (user configured) & - IP address (user configured or automatically via for example DHCP) Step 7 will take care of this for you as a long as PN Controllers (CPU's) and PN Devices are configured within the same Step 7 project. If this is not the case, you must manully take care of this and below are a few supporting links with more on this subject: SIMATIC PROFINET System Description How can you conveniently change the IP parameters and PROFINET IO device names using a program in STEP 7 V5.5? How do you reset the IP address and device name of an I device? I hope this helps |
|