(0)| 8/12/2012 6:22 AM | |
|
Posts: 1121 Rating:
|
Hi What does the diagnostic buffer say about the fault indication. It will be better if you can tell about that Have fun... |
| 8/14/2012 9:34 AM | |
|
Posts: 94 Rating:
|
Hi Khashayar, Please check the earting point. earth cable is connected properly in the earth pit or not. This incident can happen if there is EMI problem appeared. You also check the profibus cable routine. Is it going parallaly with the 415v 3phase line anywhere in the plant? Please also check the panel earth point. If possible connect the profibus shield in the earth bus. Best of luck Titas |