My customer is trying to connect an S7-200 to a Comfort Panel via ethernet. What is the correct TSAP for this? |
Last edited by: cbcX at: 12/3/2012 4:08 PM |
|
| 12/3/2012 5:08 PM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Have a look at: How do you configure communication between WinCC flexible Runtime or a Windows-based operator panel and an S7-200 (CP 243-1) via Ethernet? Regards, Marcjan |
Last edited by: Marcjan at: 12/3/2012 8:02 PMfixed link :-( Problem solved? |
|
| 12/3/2012 5:15 PM | |
|
Posts: 43 Rating:
|
I get an Error 404 when I click the link above. |
| 12/3/2012 5:24 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello cbcX; I also got a connection error froMarcjan's link above. I located the same FAQ by searching for "S7-200 Ethernet Operator Panel" using the searchbox at the right of this page, and copied the link. Try the search yourselfif the link below gives you trouble. http://support.automation.siemens.com/WW/view/en/19724696 Hope this helps, Daniel Chartier |
This contribution was helpful to
|
|
| 12/3/2012 5:39 PM | |
|
Posts: 43 Rating:
|
Many Thanks, the new link worked... |