(0)| 1/10/2013 7:05 AM | |
|
Posts: 8092 Rating:
|
Hello, Does the system display alarm no 2110? Is it PCU20 or PCU 50. Please check the surrounding temp as well as fan function. |
| 1/10/2013 10:24 AM | |
|
Posts: 8092 Rating:
|
Hello, Do you mean to say on OP Oragnge TEMP LED lits on without any alarm & your machie runs OK? Can you provide the detail MLFB number of PCU & OP? |
| 1/11/2013 9:21 AM | |
|
Posts: 8092 Rating:
|
Just clean PCU & OP unit with small vaccum blower or air blower. Might be some conductive dust short may cause orange temp LED to lit. |
| 1/18/2013 5:00 AM | |
|
Posts: 8092 Rating:
|
I would recomend you to replace PCU50 & not the processor. The LED is on OP & itwill not be visible. |
| 1/21/2013 7:41 AM | |
|
Posts: 3 Rating:
|
Sigh... I know the diode is on OP. I want to know where is SENSOR that controlls it. The sensor must be in the PCU on motherboard.
|