Hello, Try with a reset to factory settings: How do you do an operating system update (OS update) on operator panels? Regards, Marcjan |
|
Problem solved? |
|
| 2/26/2013 7:21 PM | |
|
Joined: 3/21/2006 Last visit: 1/10/2026 Posts: 10247 Rating:
|
Yes, now is clear. In case CPU goes in STOP the panel lost communication with host (CPU). It might be useful - http://support.automation.siemens.com/WW/view/en/33118312 You must fix the error which was the reason for CPU going in STOP. Downloading the OB121 just keep the CPU in RUN. Take a look in Diagnostic Buffer to understand what is wrong there in order to fix it. We can help you of course in case. Best regards, Hristo Mihalev |