(1)| 6/23/2013 10:12 PM | |
|
Posts: 138 Rating:
|
Good day sir, I am using S7-200 PID for the first time and i am facing problem in implementing it. My application is very simple and for testing of PID only i prepared a test program which is attached. I have a pump with VFD operated. The purpose of pump is to maintain the setpoint pressure in the line. I have following inputs and outputs which i tested perfectly. AIW0 ----- Feedback signal 0-10V for pressure (0-10 bar) AQW2 ----- VFD speed signal (0-10V) Q0.1---- VFD start command Now before i start the PID i tested the pump with the analog signal AQW2 and it was runing ok. And also in the mean while i was able to read the correct pressure in the line at AIW0. Then i started the PID.. i noticed that the PID gives running command approximately 40% to the VFD however the setpoint is never achived. Infact it maintains the pressure at around 1.5 or 1.6 bar when setpoint is feed 3.0 bar. I can't understand this behaviour of PID. And once i put on auto-tune it behaves the same. Can any one tell me what's wrong in the test program. Your prompt response is highly appreciated. Best regards, Hike
Attachmenttest_PID.zip (630 Downloads) |
Last edited by: Hike at: 6/23/2013 11:02 PMTest Program attached |
|
| 6/23/2013 10:42 PM | |
|
Joined: 4/20/2007 Last visit: 1/2/2026 Posts: 731 Rating:
|
please do attach your sample program |
| 6/23/2013 11:20 PM | |
|
Posts: 138 Rating:
|
sample Project uploaded. |
| 6/24/2013 12:55 AM | |
|
Joined: 5/28/2008 Last visit: 1/14/2026 Posts: 4522 Rating:
|
Please attach your program here.
|
|
Ayman Elotaify |
|