Is it possible to connect HMI client station in profibus DP network...? |
| 6/27/2013 7:05 AM | |
|
Posts: 1064 Rating:
|
yes as long as you have a profuibus card in the hmi .which hmi are you thinking about ?? |
| 6/28/2013 4:45 PM | |
|
Posts: 54 Rating:
|
My HMI station having Profibus CP card and WinCC 7.0 sp2 windows 7 ultimate OS desktop. |
| 6/28/2013 6:09 PM | |
|
Posts: 54 Rating:
|
Asking about WinCC SCADA... |
| 6/28/2013 7:02 PM | |
|
Joined: 9/27/2006 Last visit: 1/21/2026 Posts: 12481 Rating:
|
Hello pk2; I'm afraid not, MPI is not supported by the OLM. This is explained in the following FAQ: Setting up an MPI network with PROFIBUS OLMs Your best optionwould be to create a Profibus-DP channel in WinCC, tranfer your MPI tags inside it and then connect to the optical Profibus network. You can use the WinCC Tag Import/Export tool to transfer your tags from the MPI channel to a Profibus-DP channel (in the Simatic S7 Protocol Suite). WinCC Tag Import/Export Problem Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 6/28/2013 7:03 PM |
|