(0)| 6/30/2013 4:08 AM | |
|
Posts: 1064 Rating:
|
http://support.automation.siemens.com/WW/view/en/1137086 According to the manual page 1-5 it is not possible to connect this panel to s7 plc's |
| 6/30/2013 4:13 AM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello Loret; Sorry, the OP 17/PP is not designed to connect to a S7 PLC, only to S5, TI 505 and certain non-Siemens PLCs over a serial link. See the following manual, and the table of comm selections in the attachment below. OP7, OP17 Operator Panel |
This contribution was helpful to
|
|
| 6/30/2013 4:59 AM | |
|
Joined: 8/8/2012 Last visit: 3/26/2025 Posts: 34 Rating:
|
thankx all for rapid response I was hoping to find out some trick or update software make me happy with this op. regards |
| 6/30/2013 6:59 AM | |
|
Posts: 1064 Rating:
|
Sorry you didn't get the answer you wanted but that is an old unit and obsolete |
| 7/1/2013 8:09 AM | |
|
Posts: 642 Rating:
|
Hello, you need a 6AV3617-1JC20-0AX.. or6AV3617-1JC30-0AX.. If you don't have this then i would use an actual HMI-panel. Regards