I have 314C-2ptp, 343-1 v2.0 and et200s. In on-line i see station1 ( ET200S- god work ), but i don't read input and write output. Why? |
| 8/16/2007 11:08 AM | |
|
Joined: 4/6/2006 Last visit: 11/21/2025 Posts: 604 Rating:
|
Dear klakier1, Have you already integrated the PNIO_Send and PNIO_Receive blocks in your program? When a CP343-1 or CP343-1 Adv. is PN IO Controller it's necessary touse these blocks to read and write in- and outputs. It's pretty eay to configure these blocks. More information can be found in the following link. Page 38 and further. Manual CP343-1EX30 |
|
Best regards, |
|
| 8/17/2007 12:13 PM | |
|
Joined: 9/1/2005 Last visit: 1/9/2026 Posts: 4114 Rating:
|
closed cause question posted twice. The second topic with all answers and with the subject 343-1+ ET200s + profinetis published within the conferenceDecentral Peripherie. Best regards CS Moderator |
|