hi Forum I have cpu-224 plc and want to connect "4" incremental encoder's to it, for the same i have attached the datasheet of t encoder. please tell how do i use these encoders to count the pulses, how to make the connections of encoder with the cpu, will i require some extra hardware to connect all the 4 encoders. Please give any manual or such, so that ill read and configure it. Sorry lots of questions i asked?? i wana use these encoders for packaging machine project. Please help Attachmentencoder.pdf (362 Downloads) |
| 1/20/2014 10:24 AM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, You can connect 4 encoders to a 224 CPU without extra hardware, but inputs reserved for the counters you cannot use for other things. I suggest the S7-200 system manual chapter 6 Highspeed counters part for more information. Regards, Marcjan |
|
Problem solved? |
|
| 1/31/2014 3:58 PM | |
|
Posts: 267 Rating:
|
Hello, I think you can use the CPU 224XP (HC4 and HC5). The can count up to 200kHz (single phase) and 100kHz (two phase = AB = for- and backwards)http://support.automation.siemens.com/WW/view/en/1109582 Table A-6 CPU Digital Input Specifications (page 398) |