Hello RKM; As our friend Eastern proposes, you would have to integrate the ET 200S gsd file in the Yogogawa profibus configuration software (I believe they use Sycon), after which you can select the IM 151-x as a Profibus slave. You then attach the requisite number of IO modules of the ET 200S as per your actual configuration, and set the addresses that will serve to interface with the Yokogawa master. Please refer to the documentation for the Yokogawa Profibus configurator for details on the procedure. You can find the ET 200S gsd files in ths Dowload page from Siemens Support: PROFIBUS GSD files : ET 200S Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 3/5/2013 7:23 PM |
|
This contribution was helpful to
|
|
| 2/3/2014 6:46 PM | |
|
Posts: 340 Rating:
|
new question is splittet to communicate from my Yokogawa DCS ALP111 to Siemens PLC IM 151-8 |