(0)| 6/1/2014 12:13 PM | |
|
Posts: 8 Rating:
|
I NEED SAMPLE PROGRAM TO USE ENCODER FOR DETECT MOTOR SPEED USING COUNTER MODULE 6ES7 138 4DA04 0AB0C REGARDS |
| 6/1/2014 2:08 PM | |
|
Joined: 5/28/2008 Last visit: 1/21/2026 Posts: 4522 Rating:
|
Helloeng_samp, You have to use6ES7 138-4DA04-0AB0M instead of 6ES7 138-4DA04-0AB0C. The part number of 1-Count module is “6ES7 138 4DA04 0AB0” and In HW Configuration, you select between M, C or F · M: Measurement mode; used for measurement of rotational speed, frequency and periodic measurement. · C: Counter Operation; used for periodic counting. · F: Fast Mode; used for fast counting applications. So you have to select the module with index “M” instead of index “C” Attached picture will help you. Hope this helps. |
|
Ayman Elotaify |
|
This contribution was helpful to
|
|
| 6/1/2014 2:26 PM | |
|
Joined: 11/21/2007 Last visit: 1/8/2026 Posts: 2327 Rating:
|
Hello eng_samp Pl find attached the extract from the Counter module manual for rotational speed measurement. Hope this helps Cheers Navnag Attachment1COUNT_Speed_Measurement.pdf (1398 Downloads) |
|
There is no such thing as the last bug in a program |
|
Follow us on