Hi, The above answer is not correct. As the mentioned DS is not normal motor starter and contactor. Please read my detailed answer bellow.
Hellofschwa, F-DS1e-x 2.4-16A HF is an ET-200 S Fail Safe, Direct Starter (2.4-16A) configurable, High Feature type. To work with this Direct Starter, you have to know the process image input and output. Please have a look on the attached pdf file. For your case, the address used for Process Image Input is (I 120.0 to I 121.7). According to tables in the attached pdf file, I 120.1 : Motor On (0: Off; 1: On). Please take into consideration, that this signal is will change to 1 if the motor current is >18.75% of the set rated current. Hope this helps. AttachmentET200SM_e_PI.pdf (430 Downloads) |
|