Hello ronny.dp no smoking gun, but suggest you check chapter 7.2 of the SIMATIC Distributed I/O System Fail-Safe Engineering ET 200S Distributed I/O System manual (switching grounded loads,crosstalk as well as too short readback times with inductive loads can all cause this error). I hope this helps and please let us know what you find |
|
Cheers |
|
| 8/22/2014 3:33 AM | |
|
Joined: 10/7/2005 Last visit: 1/22/2026 Posts: 3054 Rating:
|
You are correct Ronny, readback time can only be set for DO0 and 1, but NOT DO2 (aka P1/P2and I somewhat missed that info in your original post). |
|