(0)| 9/1/2014 1:24 PM | |
|
Joined: 4/8/2009 Last visit: 11/15/2025 Posts: 13 Rating:
|
Hello. Accordingthis document "file_2575", page 17 , the maximum number of inputs and outputs is : Digital inputs/outputs/max. number of channels with expansion modules 48/46/94. But in the manual 6ES7212-1BB23-0XB0 , page 3 , available number is : Digital inputs/outputs, max. 78 ; max. 40 inputs and 38 outputs (CPU + EM). Why is there a difference? Which is true? Attachmentfile_2575.pdf (450 Downloads) |
| 9/1/2014 2:10 PM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, The manual is right, see link (TAB technical details) CPU 222, AC PS, 8DI DC/6DO RELAY Why it's wrong in the flyer, don't know. If this is a new project i would not go for a 200 CPU, because as you can read in the same link, the 200 is in the Discontinuation Fase. A 1200 would be a better option. Regards, Marcjan |
|
Problem solved? |
|
This contribution was helpful to
|
|
Follow us on