(0)| 6/15/2010 8:46 AM | |
|
Joined: 5/28/2008 Last visit: 1/22/2026 Posts: 4522 Rating:
|
Hello sehgal, I think there is two ways to switch analog between set point values. 1. You can do it using only one AO (of the PLC) connected to AI ( of the MM440). When the first condition that should activate the 1 set point happen, you will move the required value to the AO. And the same thing for the second value. So you will work in the PLC program. Parametrs of the MM$ will b P0700 = 2 & P1000 = 2 2. To use CDS. Make two CDSs first will work with AI1 and the second will work with AI2. P0700[1] = 2 P1000[1] = 2 P0700[2] =2 P1000[2] = 7 Hope this helps. |
|
Ayman Elotaify |
|
| 6/15/2010 11:34 AM | |
|
Posts: 101 Rating:
|
The easiest way is to use an analog switch found in the free functions. You will need a binary input to select which switch input you wish to use. |
| 9/11/2014 11:00 AM | |
|
Posts: 4757 Rating:
|
follow up question published by Bhavin2talis split to a separate thread with the subject where i can find this analog switch?. Best regards Min_Moderator |