(0)| 12/29/2014 11:43 AM | |
|
Posts: 54 Rating:
|
I use analog input moduleAI8x13Bit (6ES7 331-1KF02-0AB0). I set the input to 4-20mA. What is the range I read in the PIW? Is it 0-32767?
|
| 12/29/2014 11:50 AM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, 0 to 27648, see SIMATIC S7-300 S7-300 Module data, chapter 5.1, Table 5-9 Regards, Marcjan |
Last edited by: Marcjan at: 12/29/2014 11:53 AMProblem solved? |
|
Follow us on