1/11/2015 9:08 PM | |
Posts: 87 Rating:
|
Hi. You need have the same configuration in the drive side with the same telegram, look the attachment for you check the address. But If you want change the address you can try make a change in the DP Slave properties -> Configuration -> Details. In generally in the telegram 2/2 the first PZD (first word) is the control word and the second PZD (second word) is the setpoint For example: PLC -> Drive : PQW 256 := Control Word. PQW 258 := Setpoint. Drive -> PLC PIW 256 := Status Word; PIW 258 := Actual Value (in generally Speed)
AttachmentHW for G130 CU320-2DP.pdf (305 Downloads) |
1/11/2015 11:48 PM | |
Joined: 11/25/2013 Last visit: 4/9/2025 Posts: 35 Rating:
|
Thank You Sir I set the Vector-02 at Drive
and Please can you send me the address Name for Status and control word. |
1/13/2015 11:45 AM | |
Posts: 87 Rating:
|
Hi. The PROFIBUS Address are correct? p0918 = the same address that you set in the HW. DriveUnit(Your Drive) -> Control_Unit -> Expert list -> p918 See attached an explanatory document, maybe help you. Hope this help you. Regards.
AttachmentG130.zip (240 Downloads) |