(0)| 1/14/2015 8:24 PM | |
|
Posts: 5225 Rating:
|
..if still having problems: Please inform us which software and version? w
|
| 1/15/2015 3:59 AM | |
|
Posts: 291 Rating:
|
Which Simatic Manager version you are using? it may be the older one and may not have required module. |
| 1/15/2015 10:16 AM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Please give us the complete hardware setup (print screen) Are you trying to insert a module for a remote rack (ET200M) in a local rack? That is not possible, you need other modulethen. Regards, Marcjan Attachmentmodule.pdf (313 Downloads) |
Last edited by: Marcjan at: 1/15/2015 10:29 AMLast edited by: Marcjan at: 1/15/2015 10:23 AMProblem solved? |
|
This contribution was helpful to
|
|
| 1/15/2015 12:02 PM | |
|
Posts: 6 Rating:
|
Sorted...Thank you Marcjan. |
This contribution was helpful to
|
|
Follow us on