(0)| 11/9/2015 7:13 AM | |
|
Posts: 32 Rating:
|
Dear Sir, I have a system where 3nos. of 1200KW,690Volt line supply (AIM+ALM) in parallel and are controlled by one CU320. I have commissioned the system and was running fine in parallel operation. Few days back, i got the following faults during start up:- F06200(Infeed: one or several line phase failed) A06205(Infeed: Voltage dip in at least one line supply phase) F06210(Infeed: Summation current to high) I checked the message and then as per message help, checked all the fuses, line supply connection cable tightness, supply voltage amplitude. All are found ok as per my test. Then i switched off electronics and switched on after one hour and when i have given the on command for parallel ALMs, all are started and pulses are enabled for all three. After one day, again i got the same fault and warning during starting. But after several trying, i was able to start the ALMs. Since then this problem continued often during start up but not all the time and after several start- Stop attempt along with the elctronics power restart, it eventually does get on. I did not able to solve this issue since then, Is it the product problem or any specific hardware fault? Even i tried to start all the (AIM+ALM) individually at least for 10 times each and in all the time i got success. Please help to sort out the issue. Thanks in advance. With regards, Anirban Mandal AttachmentEDGER.pdf (188 Downloads) |
Last edited by: Min_Moderator at: 11/9/2015 10:48:29 AMContact data removed |
|
| 11/12/2015 11:19 AM | |
|
Posts: 32 Rating:
|
Dear All, Is there any solution of this problem?? Did anybody face this problem?? Please suggest. Regards, Anirban Mandal |