Hello, a manually start/stop of the FAN is not possible. Regards Christoph |
| 1/6/2016 9:59 AM | |
|
Joined: 4/28/2009 Last visit: 6/3/2025 Posts: 347 Rating:
|
Hello, relays for fans are switched from X272 connector on PSB (power supply board), which is located on left side of drive. It is together with CIM (control interface module), where are connected all cables from other parts of drive (optical cables, signals from current transformers, etc.). CIM module is mounted on PSB board. 24V power supply is located on this PSB board. 24V is generated from DC link voltage or from pins 1 and 2 in X9 connector, which is under fuses and relays for fans. So if all fans don't rotate, PSB board could be defective. There is a fuse on this board, but I don't know if it is in power supply circuit, you can check this fuse. Or there could be defective fan relay, fan transformer or wiring between. Order number for fan transformer is not easy to find without order number of whole drive. You can get list of drive parts entering drive order number to SparesOnWeb system: www.automation.siemens.com/sow. With regards |