Dear Sir, We ordered FUH1010, 7ME3603-3CA00-1PP2-Z K02+K02+R02 last year for crude oil application. As per selection it came with 1no. RTD. We have commissioned both the channels in Direct Mode and clamp on RTD was installed on pipe and cables are connected on 1010N-5*S2 on TB1. Now the flow is showing facing following issues: 1. Flow rate is varying about 3.25% on average against existing coriolis flow meter. 2. RTD inputs are not showing any variable values diagnostic screen. 3. Is it possible to configure Analogue output from FUH1010 for Temperature to control panel as ordered extended i/O option? 4. Difference between path 1 and path 2 is about 5%. Flow rate is going in sinusoidal form but in opposite direction., like path 1 is 105m3/h then path 2 is 100m3/h and when path1 is 100m3/h then path2 is 105m3/h. Is is acceptable by API? 5. We tried to active the table for Liquident but it is not showing any K0 or K1 values to enter. 6. Viscosity shown in diagnostic screen is 10times more than what we entered in configuration. Please support us to close this subject. Regards, Davinder Singh