(1)| 6/16/2015 2:18 PM | |
|
Posts: 5521 Rating:
|
hi Jon, have you checked the wiring of the module. the Diagnostic message in the manual that is nearest to your failure says: Diagnostic message: No external auxiliary voltage Possible causes ot the Problem: Module supply voltage L+ missing Corrective measures: Connect supply voltage L+ You can also see the manual for your self to check the whole wiring for each chanel and possible application: SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modules |
| 3/21/2016 9:34 AM | |
|
Joined: 3/2/2007 Last visit: 1/14/2026 Posts: 1002 Rating:
|
important information. thank you |
|
... thank you ... |
|