(1)| 8/29/2016 1:57 PM | |
|
Joined: 10/26/2011 Last visit: 1/13/2026 Posts: 766 Rating:
|
Yes, for archiving data for more than a year, you have to use the Process Historian. For the Process Historian, you have to use a separat station (no OS client or ES allowed; but you can use the Information Server or Maintenance station on the Process Historian station. Note, on the Process Historian Station you don't have WinCC. NOTICE: You cannot buy the Process Historian without a product consultation and a special release by the product manager for Porcess Historian.
|
Last edited by: Thunderstorm at: 8/29/2016 2:02:05 PMSIMATIC PCS 7 - Overview |
|
| 10/24/2016 1:37 PM | |
|
Joined: 5/20/2015 Last visit: 11/6/2025 Posts: 34 Rating:
|
Hi Myst, I think 1024 byte is average memory requirement per message, And its mentioned it will vary with languages. 4096 bytes for all 5 standard languages. Yes its bit confusing, kindly see the attachment for your reference. calculation also showed in it. AttachmentPH_Alarms_Memory_Requirements.zip (383 Downloads) |
This contribution was helpful to
|
|
Follow us on