Hrello dado; All ypur LEDs are active for connection side #2, SF is active on connection side #1. There are probably many errors you have to check in your configuration. - first, check whether the addresses you set on the DIPswitches are valid, they must match your Profibus slave configuration. Right now, slave 1 is at adderss 12, slave 2 is at address 3. - second, your DIA switch is set on each side, do you really want the complete diagnostics fr the module? Read the notice in the attachment below. - third, explaon how you have setup the data exchange zones on each side of the slave. Note that they have to be inverted but in the same order and size: on side 1, for example, 8 Bytes OUT, 16 Bytes IN on side 2, (reversed), 8 Bytes IN, 16 Bytes OUT You will find all required details in the DP/DP coupler manual: https://support.industry.siemens.com/cs/fr/en/view/1179382 Hope this helps, |