(0)| 4/13/2017 7:24 AM | |
|
Joined: 5/15/2010 Last visit: 7/4/2025 Posts: 172 Rating:
|
Hi Experts, I have a problem where all LED of PLC are on. Can i assume the PLC is gone? |
| 4/13/2017 7:46 AM | |
|
Joined: 5/15/2010 Last visit: 7/4/2025 Posts: 172 Rating:
|
The CPU was running from past 8 years ans suddenly this problem occurred. |
| 4/13/2017 8:04 AM | |
|
Joined: 5/15/2010 Last visit: 7/4/2025 Posts: 172 Rating:
|
Yes for me too in 300 |
| 4/16/2017 8:10 AM | |
|
Joined: 5/15/2010 Last visit: 7/4/2025 Posts: 172 Rating:
|
Hi, This means firmware has vanished? How can i update firmware in this case? |
| 4/16/2017 3:42 PM | |
|
Joined: 3/28/2015 Last visit: 1/4/2026 Posts: 727 Rating:
|
Hello, Perhaps one of the following points might solve the problem: 1-Check the Back plane between CPU and Rack . 2-Check the connections. 3-Post the diagnostic buffer of the CPU. 4-Perform Master reset for the CPU. 5-Upgrade the firmware of the CPU. Where can you find the latest updates of the operating systems for the CPUs S7-31x, IM15x and BM147? 6-Kindly have a look at the attached file. AttachmentDiagnostics and operating system firmware.zip (429 Downloads) |
|
Eng.Mohamed Ibrahim |
|
This contribution was helpful to
|
|