Hello, I am having problems with SF led light on S7-300 PLC. I am using one PLC to control two drives via PROFINET IRT. Drives have been commissioned via STARTER and TIA Portal, and are working and communicating fine. I uploaded some pictures and diagnostics buffer. Equipment used:
Is there something I can do? Bruno AttachmentError.zip (399 Downloads) |
| 5/6/2017 2:20 PM | |
|
Posts: 387 Rating:
|
Hello, you PC IP address seems to be conflicting with any of the other device. Please check it. Kbv. |