hello,
I have a CPU 315 2DP which is defaulted after loading a program. It appends the diagnostic report thks Attachmentdiagnostic.docx (408 Downloads) |
Last edited by: Min_Moderator at: 6/13/2017 12:35:40 PMAdjust formatting |
|
| 6/13/2017 12:57 PM | |
|
Posts: 5521 Rating:
|
hi, It would be easier to have the diagnostic buffer in english, but I think I got it anyway. The first entry is a Stop-intruction from the programm. I guess there are problems with the Failsafe-programm. Have a look in FB273 or in the FB where FB273 is called. Second entry is a internal CPU-error, when instance-DB 551 of the F-FB is called. Both entries are in caused by the same error. You can try to update the FW of the CPU. the latest FW-Update can be downloaded here: Operating System Updates for CPU 315F-2 DP (6ES7315-6FF04-0AB0) hope this helps, regards, |