Hello e.bogatian, F60057 = Armature current sensing fault. r50047(2) current sensing value seems to be problematic. Have you checked CT? Please check CT resistance at X7:1 & 2 as well as X8:1 & 2 terminal. If both are OK, check load resistor (10 ohm) on power interface card i.e. C98043-A710x. Other wise try by replacing power module card. HTH. |
This contribution was helpful to
1 thankful Users |
1/17/2018 1:21 PM | |
Joined: 10/29/2015 Last visit: 1/15/2024 Posts: 5 Rating:
|
Tks folk! resistance is ok. 10ohm is also ok. now i will test drive injecting current in the laboratory |