(1)| 3/2/2018 9:27 AM | |
|
Posts: 8092 Rating:
|
Is it new machine under commissioning or old machine? Which is value in P0860? How the infeed module line supply contactor is controled? |
| 3/3/2018 9:10 AM | |
|
Joined: 1/17/2013 Last visit: 1/13/2026 Posts: 1117 Rating:
|
Dear PISCEAN 2010, The problem from NC contact of infeed magnetic have problem. I have changed new one and F7300 removed. I need to know more as previous picture. What is Line contactor enable ? Is it hardware or software ? What is Line contactor enable IN and OUT signal ? What is Infeed enable OUT signal ? Best Regards, Vorapob |
|
Best Regards, |
|
This contribution was helpful to
|
|
| 3/3/2018 9:44 AM | |
|
Posts: 8092 Rating:
|
Hello, Nice to learn your problem is solved. In your attached picture, Line contactor enble block is software & physical wiring of contactor NC is hardware. Line contactor enable IN OUT signals are DI/DO inacse of hardwiring where as in case of profidrive/profinet communication, it is bit tranfer via control word & status word. Infeed enable output signal indicates close loop operation completed & needs to configure in further logic. Please download & refer SINAMICS S120/S150 manual, chapter Function diagram, 3.10 sequence control to understand answers of your questions. HTH. |