(2)| 3/21/2018 9:42 AM | |
|
Joined: 4/28/2015 Last visit: 11/27/2025 Posts: 10970 Rating:
|
Hello, all depends to specific CPU, check connection resources. Generally if we ommit any other communication created in your prj, 16 devices can be connected. Therefore that message about 4 devices out of permission range. In my opinion, on S7-1200 there isn't other solution with expand of HW which can add more resources. My opinion. Solution can be maybe cut your profinet network and add another S7-1200 with rest or required number of Profinet devices. Then use of some S7 communication f.ex. if you need exchange some data between CPUs. Check this link (standard): CPU S7-1215 specification Or another solution is S7-1500, check required type of CPU which can handle 32 devices. |
Last edited by: Duris_I at: 3/21/2018 9:44:26 AMLast edited by: Duris_I at: 3/21/2018 10:09:41 AMLast edited by: Duris_I at: 3/21/2018 10:13:39 AMLast edited by: Jen_Moderator at: 3/21/2018 11:08:10 AMOptimized link. With best regards... |
|
This contribution was helpful to
|
|
| 3/23/2018 3:16 PM | |
|
Joined: 4/28/2015 Last visit: 11/27/2025 Posts: 10970 Rating:
|
You're welcome and good luck. |
|
With best regards... |
|
Follow us on