(0)| 7/8/2018 7:24 AM | |
|
Posts: 8092 Rating:
|
Hello, Which infeed module is used? Have you chceked if infeed ready p0864, main contactor ON feedback, signals are present? |
| 7/8/2018 7:35 AM | |
|
Posts: 33 Rating:
|
Thanks 🙏 to interest me Infeed is external supply dc but is good he given 600 vdc on plug input to drive what can I do to remove these falut |
| 7/9/2018 7:43 AM | |
|
Joined: 10/11/2006 Last visit: 1/21/2026 Posts: 6052 Rating:
|
Hello, as PISCEAN mentioned already: You have to connect p864 at your drive object. This parameter gives the motor module the information, that the infeed is enabled (ususally you have a normal infeed which gives a "1" signal to this parameter in the motor module, to show that the infeed works). In your case you need to think of some feedback to give a "1" signal to p864 from your external infeed. (hint: if you ensure during testing, that your infeed works fine you could give a fixed "1" to p864, but I do not recommend this for the later normal operation of your machine - than you should use some feedback signal from your infeed) |
|
With best regards, |
|
This contribution was helpful to
|
|
Follow us on