Joined: 9/27/2006 Last visit: 1/20/2026 Posts: 12481 Rating:
|
Hello Lindy; You are correct in your assumption that power cables should be kept at a distance from Profibus cabling, even if the Profibus cable is properly grounded and earthed. See thie screenshot below, taken from the Procetec Profibus FAQs: https://procentec.com/service-support/faq/profibus/ You can find more precise distance tables from the Profibus Design and Profibus Installation document downloads, from Profibus.com. https://www.profibus.com/download/profibus-installation-guidelines/ That being said, you should also check the diagnostic buffer of your PLC (if it is a Siemens S7, you guive no make or model information) for details of the affected nodes. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 7/24/2018 2:11:08 AM |
|