Hey. We are currently trying to fix the error 60300. We have a crane application. Reversible drive. We intend to change the parameters of p50179, p50161, p50160. This will reduce the current during the transition from motor to generator mode and back. ------------------------------------------------------------------------------------------ |
Last edited by: LehaPetyhov at: 10/24/2018 5:52:50 AMLast edited by: Jen_Moderator at: 10/24/2018 7:19:10 AMNew subject after splitting |
|
| 10/24/2018 7:34 AM | |
|
Posts: 2 Rating:
|
The problem is solved by setting the values of parameters 50160 = 0.1; 50179 = 5; 50161 = 5 |