(0)| 1/1/2019 11:54 AM | |
|
Joined: 4/17/2018 Last visit: 6/23/2025 Posts: 262 Rating:
|
Hello Chriss, SIMATIC S7-1200 can be operated as PROFINET controller as well as PROFIBUS master (with CM 1243-5). A SINAMICS G110M or G120 shall be connected as as PROFINET device or as PROFIBUS slave. read this link for more information. -> Not only siemens drives, if you have another drive you can connect it to s7-1200 only you have to install its GSD file. see this example. I hope this can help you regards. |
| 1/2/2019 9:58 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello Chris; In that case, the Multi-Ethernet option card manual might interest you, if the drive you are planning to use is a EFC 6160 or 5160: https://inverterdrive.com/file/Bosch-Rexroth-Multi-Ethernet-Manual Chapter 5 discusses Profinet, including drive parameters, the download location of the GSDML file for the drive and an example code with a S7 PLC. Hope this helps, |
This contribution was helpful to
|
|
| 1/2/2019 11:18 PM | |
|
Posts: 99 Rating:
|
Thanks very much. I usually buy Rexroth drives from inverterdrive.com |