Hello everyone, There's a test project a purpose of which is:
At the same time there's a need to forward a Byte:
Could anyone give an advice in terms how to organize it in a better way. Msorich Attachmentconception_question.pdf (270 Downloads) |
| 1/23/2019 12:54 AM | |
|
Joined: 9/27/2006 Last visit: 1/20/2026 Posts: 12481 Rating:
|
Hello msorich; Your program confuses me, and I have a feeling you are confusing the Step 7 compiler as well. Are you trying to write from PLC1 to a DB in PLC2? And are you trying to read from a DB oin PLC2 to PLC1? This would not work. Look at the hardware configuration of the DP/DP coupler, you will see that in each PLC,s hardware configuratio there are only I and Q addresses for the coupler. And you must use I and Q addresses in each PLC's configuration. Look at the following drawing, demonstarting the data exchanges when using a DP/DP coupler between 2 DP-masters. And study the DP/DP coupler manual and FAQs, they would be very useful at this time. DP/DP Coupler manual: https://support.industry.siemens.com/cs/ww/en/view/1179382 What are the special features of input/output addressing with the DP/DP coupler? https://support.industry.siemens.com/cs/ww/en/view/22327981 Configuration of the I/O Data on DP/DP Coupler https://support.industry.siemens.com/cs/ww/en/view/19281019 Once the data transfer is executed using I and Q addresses, you can use Move and Blockmov functions to transfer the data to and from local DBs. Hope this helps, Daniel Chartier |