Hello, But you can use an one wire connection connected to STO_A & STO_B if the components are in one cabinet, check chapter 4.4.3.2 of the safety integrated manual. |
|
With best regards, |
|
| 3/18/2019 11:46 AM | |
|
Posts: 413 Rating:
|
thanks, I'll do it, connect two channels STO_A&B to one NC contact (as attached), only I will use a normal relay (not emergency) |