Hello dear friends. I have 315-PN/DP CPU and I Have WAGO 750-343 Configurationis O.K. But I can't use DI/DO. How to use DI / DO ? |
| 7/10/2019 3:30 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello avatar; I do not see in your configuration (HWConfig or physical) a required end-module, 750-600. It is necessary to have such a module at the opposite end of the coupler's mechanical installation, to close the backplane bus. See the attachment below, showing a sample configuration for the 750-343, taken from the 750-343 manual. https://www.wago.com/global/d/1218 Start by procuring and installing the end-module, If you still cannot see the I/O modules, then we need to investigate your installation further. Hope this helps, |