Hello, you use TO (Positioncontrol) with a not isochronous communication. You have a chitter on setpoints and actual values. So you have a worse control behavior and your velocity in trace shows the jitter, too. Do a trace of the velocity in G120. The following application in chapter 3 shows how to improve the control behavior. 3. Basics https://support.industry.siemens.com/cs/ww/en/view/109743917 When the reachable accuracy don't suit for your application, it is possible to use basic positioner. SINAMICS G: Axis positioning with the "SINA_POS" block https://support.industry.siemens.com/cs/ww/en/view/109736845 |
|
With best regards, |
|
| 8/13/2019 11:40 AM | |
|
Joined: 10/11/2006 Last visit: 1/21/2026 Posts: 6072 Rating:
|
Hello, you need a license for the usage of the basic positioner in CU250S-2. That's why you get the license warning. The license installation is described in the manual of CU250S-2: https://support.industry.siemens.com/cs/ww/en/view/109757229 |
|