Hi, yes you can use telegram 352 for that, but not with SINA_SPEED FB (this one is only for telegram 1). Use the block for telegram 352 from the LSINAExt library: https://support.industry.siemens.com/cs/ww/en/view/109747655 This one is the right for you ;) |
|