(0)| 1/7/2020 11:37 AM | |
|
Joined: 10/11/2006 Last visit: 1/16/2026 Posts: 6068 Rating:
|
Hello, in your case I think that the only possibility is the jogging mode. Commands "Jog 1" or "Jog 2" switch the motor on and off automatically and as soon as the motor is on, the motor accelerates to the setpoint, jog 1 or setpoint, jog 2. The two different setpoints can, for example, be assigned to motor clockwise and counter-clockwise rotation. Parameter Description p1055 = 722.0 Jogging bit 0: Select jogging 1 via digital input 0 p1056 = 722.1 Jogging bit 1: Select jogging 2 via digital input 1 p1058[D] Jogging 1 speed setpoint p1059[D] Jogging 2 speed setpoint
Have a look at chapter 6.3.8 of the following manual: https://support.industry.siemens.com/cs/ww/en/view/109769350 |
|
With best regards, |
|
This contribution was helpful to
|
|
| 1/13/2020 12:44 PM | |
|
Posts: 24 Rating:
|
actually i find the solution, working fine. it can be possible with macro in CU 240 E-2 Thank you, hope it help someone else |