What software and what PLC? |
| 4/23/2020 7:50 AM | |
|
Posts: 11 Rating:
|
hello, i use s7-400, step7 |
| 4/30/2020 2:01 PM | |
|
Joined: 9/27/2006 Last visit: 1/21/2026 Posts: 12481 Rating:
|
Hello HOGY: When you create a DB, you are in declaration view, and any value you write to the DB variables is written as "initial" value. These initial values are the ones that will be read in the DB when the CPU is restarted. When you go online and run the program, your functions might write in new values to the DB, known then as "actual" values. If these are the values you want to retain when you start up you CPU, follow the suggestion in the following FAQ: How can you back up the actual values of DBs and markers? https://support.industry.siemens.com/cs/ww/en/view/18778977 Hope this helps, |