12/9/2014 9:35 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
Hello. You will needOperating Instructions,List manual. Also look for application manuals that is suitable for you:
|
12/16/2014 10:18 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
Hello. What value has fault F60056, look in r949 while fault is active.
|
12/16/2014 10:38 AM | |
Joined: 8/19/2013 Last visit: 1/23/2025 Posts: 13 Rating:
|
r949 value is 9 when fault f60056 occurs.please help |
12/16/2014 10:41 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
9: Reference speed (p2000) not set (factory setting value must be modified)! |
12/16/2014 10:55 AM | |
Joined: 8/19/2013 Last visit: 1/23/2025 Posts: 13 Rating:
|
But p2000 is not accessible even in expert list what to do |
12/16/2014 11:16 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
On which drive object you try to look for p2000? This parameter is in Drive, not in CU.
|
12/16/2014 11:30 AM | |
Joined: 8/19/2013 Last visit: 1/23/2025 Posts: 13 Rating:
|
checking in drive object 1 and 2 both.... |
12/16/2014 11:48 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
If you are using BOP20 for commissioning, check p0003, p0004. |
12/16/2014 1:02 PM | |
Joined: 8/19/2013 Last visit: 1/23/2025 Posts: 13 Rating:
|
Sir how to give on command.m first time commissioning dc drives..Please ecplain |
12/17/2014 11:47 AM | |
Joined: 8/19/2013 Last visit: 1/23/2025 Posts: 13 Rating:
|
Finally my drive is working thank u siemens technical support. |
1/17/2018 1:04 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8171 Rating:
|
New question published by K K raju is split to a separate thread with the subject 6ra80 what are the required parameters to be enterednin drive to run the motor for testing purpose?. Best regards |
Follow us on