7/11/2014 12:38 PM | |
Posts: 1058 Rating:
|
Hello Kheckhec, Alarm A0703 means you have a problem with your communication Paramerters. When changing P0918, did you check if DIP switch for address is still 0? If address is set with DIP switch, then P0918 is not valid, switch has priority. If DIP switch is 0, then address defined in Parameter P0918 is valid. See documentation of Parameterlist here(alarms and failures are also described there): parameter list MM440 In case you need the manual of MM440, you find it here. regards |
7/16/2014 4:17 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello Kheckhec, Please have a look: Operating Instructions: MICROMASTER PROFIBUS Optional Board and LED in front of the Profibus optional board, what color is it? |
7/17/2014 11:37 AM | |
Posts: 10 Rating:
|
Hi SAR2013 I have set CB address in parametter P0918 as old one. I still not OK |
7/17/2014 11:42 AM | |
Posts: 10 Rating:
|
Hi eisenpferdreiter Thanks for the document. DIP switchs in new inverter are the same in old one (the broken one). I check the document but i'm not clear about that problem. Can you support to help me. Tks |
7/17/2014 11:44 AM | |
Posts: 10 Rating:
|
Hi Ste39, The color of LED in front of the Profibus optional board is blinking green |
7/17/2014 11:51 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello Kheckhec, Manual wrote: green flashing Cyclical process data exchange in progress, but setpoints invalid (control word = 0), e.g. because SIMATIC master is in "Stop" state |
7/17/2014 12:05 PM | |
Posts: 1058 Rating:
|
Hi Kheckhec, what communication module do you have in use? Alarm A0703 just refers to your communication module. You will have to look there for the problem. regards |
7/17/2014 3:14 PM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello eisenpferdreiter, I think for sure that he will be using this module, because I know that I was the only module of communication via Profibus for MM4. Operating Instructions: MICROMASTER PROFIBUS Optional Board let's see what he will answer |
7/18/2014 5:25 AM | |
Posts: 10 Rating:
|
Hi Ste39, You are right, Micromaster 4 profibus Modlue is 6SE6400-1PB00-0AA0. |
7/18/2014 8:15 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello Kheckhec, Your PLC CPU 314as it is? Is in RUN or have other LED lit? Have you tried with power OFF -->ON? Have youlooked the diagnostic buffer of the CPU? Some information? What blocks are you using to exchange data between the CPU and Micromaster? |
7/18/2014 8:17 AM | |
Posts: 10 Rating:
|
Hi Ste39 The PLC have still run, I don't understand what is happening |
7/18/2014 8:40 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello Kheckhec, Manual wrote: Parameters "P0700" and "P1000" (fast selection/process data master control) The control word and setpoint sources can be selected quickly in parameters P0700 (select command source) and P1000 (select frequency setpoint) respectively. Command source from PROFIBUS: P0700 = 6 Frequency target value from PROFIBUS: P1000 = 6 Note: P0719 must be 0 |
7/18/2014 9:27 AM | |
Posts: 10 Rating:
|
Hi Ste39 I have settup it: P0719 = 0 P0700=6 P01000 =6 Why do it not OK ? |
7/18/2014 10:21 AM | |
Joined: 1/21/2013 Last visit: 11/20/2024 Posts: 4620 Rating:
|
Hello again, 1) Have you tried with power OFF -->ON or restart your CPU? (if possible) 2) Have youlooked the diagnostic buffer of the CPU? Some information? 3) What blocks are you using to exchange data between the CPU and Micromaster? 4) The profibus module is powered? (24Vdc) 5) This drive is the last node on the Profibus network? if it is the last node, the terminating resistor must be ON otherwise OFF. 6) The ground connection is correct? Maybe in the Profibus connector does not have a good bond. Please answer these questions And have a look me or Vithany: MM440 CB fault 4 F0700 - A0703 alarm ...Help! |
Last edited by: Ste39 at: 7/18/2014 10:28 AMAdd Thread |
|
This contribution was helpful to
1 thankful Users |
7/18/2014 6:09 PM | |
Joined: 8/31/2005 Last visit: 9/12/2025 Posts: 2198 Rating:
|
Make shure your PLC sets at least Bit 10 in the control word. A control word that is 16#0000 is ignored and may cause the communication fault. |
|
|
10/27/2014 2:43 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4759 Rating:
|
|
4/24/2017 4:14 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4759 Rating:
|
New question published by BOX1 is split to a separate thread with the subject Control an MM4 drive from the S7-300 PLC. Best regards |
4/25/2017 11:25 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4759 Rating:
|
New question published by BOX1 is split to a separate thread with the subject Programming for start of engine. Best regards |
Follow us on