7/14/2021 11:44 AM | |
Joined: 9/27/2006 Last visit: 9/5/2025 Posts: 12398 Rating:
|
Hello devlooper; Are you running Simatic Manager as an administrator? Hope this helps, Daniel Chartier |
7/14/2021 12:38 PM | |
Joined: 5/27/2021 Last visit: 7/3/2022 Posts: 7 Rating:
|
Hello dchartier, Yes i did. |
Last edited by: devlooper at: 07/14/2021 12:50:09 |
|
7/15/2021 12:08 PM | |
Joined: 10/10/2014 Last visit: 8/28/2025 Posts: 1725 Rating:
|
Hi devloper What exact WinCC version do you use, what update and what Step 7 version ? Best regards schufri |
7/15/2021 12:23 PM | |
Joined: 5/27/2021 Last visit: 7/3/2022 Posts: 7 Rating:
|
Hi schufri, I use : SIMATIC Manager Step 7 V 5.6 + HF1 WinCC Explorer Runtime V7.3 + Upd1 The issue comes when I activated the WinCC (already set for pdl and tag management), suddenly the PG/PC interface is missing on my PLCSIM and simatic manager. Thank you. |
7/15/2021 12:37 PM | |
Joined: 5/27/2021 Last visit: 7/3/2022 Posts: 7 Rating:
|
Same issue posted here : https://support.industry.siemens.com/tf/ww/en/posts/pg-pc-interface-missing-when-activated-wincc/219126/?page=0&pageSize=10#post1025912 |
7/15/2021 3:40 PM | |
Joined: 10/10/2014 Last visit: 8/28/2025 Posts: 1725 Rating:
|
Hi devloper, If the PG/PC- interface is missing on you computer please install also Simatic Net on your PC With WinCC Siemens delivers also a SIMATIC Net DVD. Also I recommend you to install for WinCC V7.3 the Update 19 . https://support.industry.siemens.com/cs/de/de/view/109768972 Best regards schufri |
This contribution was helpful to
1 thankful Users |
7/15/2021 5:12 PM | |
Joined: 9/3/2008 Last visit: 8/19/2025 Posts: 938 Rating:
|
Hi, Neither Step7 5.6 SP1 or WinCC 7.3 or Simatic Net V13 is compatible with Windows 10 Pro Ver 20H2. You need Step7 5.6 SP2 or later and WinCC 7.5 SP1 or SP2. Regards |
Michael |
|
This contribution was helpful to
1 thankful Users |