5/16/2016 11:32 AM | |
Posts: 119 Rating:
|
Dear Harry, Thank you so much. I will try today and let you know if I find any problems. Salman |
5/18/2016 10:33 AM | |
Joined: 2/21/2014 Last visit: 9/12/2025 Posts: 672 Rating:
|
Hi, I see that you are trying to export 3 values to the Excel sheet from the following objects which are present in the picture opened in runtime: 1. Output value of "I/O Field1" 1. Output value of "I/O Field2" 1. Text value of "Static Text21" These should be present in the picture open in runtime. I think the code you have posted was taken from somewhere which you are trying to use. also I think it was originally not a global action. now I think based on the values you are exporting to the excel, it is better to use this action inside the Picture. please see the attachment. you can set the cyclic trigger in the same way as you did for global action. but you can use a TAg trigger also for example "M100_0" the code I attached is not exactly the same as yours... you will have to check the logic to fulfill your conditions. thanks, HarrY AttachmentVisibleTrigger.zip (465 Downloads) |
You can always use "Rate" and "To Thank" button to appreciate my efforts in helping you :) |
|
This contribution was helpful to
1 thankful Users |