3/13/2018 10:28 AM | |
Posts: 12 Rating:
|
And to configure the VW's you use the modbus properties. Do you perhaps know a good modbus simulator? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 3/14/2018 9:47:23 AMNew subject after splitting |
|
3/13/2018 4:09 PM | |
Posts: 12 Rating:
|
Did some testing but only errors. I attached a printscreen of the LOGO program and settings. |
3/13/2018 4:57 PM | |
Posts: 12 Rating:
|
Also tried to setup the connection in network-project mode. Don't understand the client and server logic |
3/13/2018 5:02 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
I made a screenvideo for you, but it is too large to attached at one file. I made a ZIP archive with 2 parts. Here part one. AttachmentModbus Test with Schneider Generic Tester.zip (647 Downloads) |
3/13/2018 5:07 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
Here comes part two. After download of part tow you must rename part two from
to Modbus Test with Schneider Generic Tester.z01 Files with extention z01 can't be attached. That's why i must rename the file with the extention zip. AttachmentModbus Test with Schneider Generic Tester.z01.zip (538 Downloads) |
3/13/2018 5:30 PM | |
Posts: 12 Rating:
|
that was very helpful. Thanks. |
This contribution was helpful to
1 thankful Users |
3/13/2018 5:32 PM | |
Joined: 12/18/2014 Last visit: 9/14/2025 Posts: 35958 Rating:
|
Hello paulusB, you're welcome... |